Commissioning with the programmer

Level: Intermediate 9 min read 45 questions

Commissioning is the moment of truth: the panel that has been built and the program that has been written meet the real machine for the first time. Things almost never all work first time, and that is fine if you work methodically. What separates a two-day commissioning from a two-week one is not luck: it is method, and above all how well the technician in the field and the programmer, often on the other end of the phone, understand each other.

The order of a commissioning

Every company has its own procedure, but the general outline is always the same: first everything is checked dead, then power is applied section by section, inputs and outputs are tested one by one, the safety functions are validated, and only then is the machine moved, first by hand and then in automatic.

1. Dead checks terminals, earth 2. Power up step by step 3. Inputs one by one 4. Outputs with permission 5. Safety E-stops, doors 6. Manual slowly, by hand 7. Automatic dry run, product 8. Handover documents, backup
The phases of a commissioning. The safety functions are validated before the machine is moved in earnest, not at the end.

1. Before applying power: dead checks

With the panel dead, you check the things that would be very costly to find later:

2. Apply power section by section

Never switch everything on at once. Power is applied to the main supply and measured: on a 230/400 V supply, about 400 V between phases and about 230 V phase to neutral. Then the circuits are closed one by one: the 24 V power supply (its output is checked), the PLC, the modules, the field devices. If something trips or smells burnt, you know exactly which circuit it was.

When the PLC is switched on, check its indicators: the CPU and the modules must show no errors. If the program is not loaded yet or the PLC is in STOP, the outputs do not switch anything on, which is exactly what you want at this stage.

3. Check the inputs, one by one

The key tool is the I/O list: a table with every signal, its PLC address, its name, what it physically is and which terminal it is on. The field technician operates each sensor or push button and the programmer confirms on screen that the right input changes. Each line is marked: correct, corrected or pending.

AddressNameDescriptionChecked
%I0.0Main_stopDesk stop push button (NC)Correct
%I0.1StartDesk start push button (NO)Correct
%I0.4Part_on_tableInductive sensor on the tableWires crossed with %I0.5, corrected
%I0.5Cylinder_upCylinder limit switchWires crossed with %I0.4, corrected

Remember how contacts behave: a stop push button, wired normally closed, has its input at 1 at rest and goes to 0 when pressed. If the programmer sees a permanent 0 on a stop, something is open: the push button itself, the wire or the common.

Typical mistakeSigning off an input because “something lit up”. You must confirm that the input on the list changes and not another one. Two wires swapped on neighbouring terminals pass this test by eye and then drive the machine crazy.

4. Check the outputs: forcing with permission

To test an output without running the whole program, the programmer switches it on from the computer. Two things must be kept apart:

Forcing an output really moves the machine, bypassing the program logic, including any interlocks the programmer has written. That is why there are rules that are not up for discussion:

  1. The field technician gives explicit permission for each force, after checking that the area is clear.
  2. One output is forced at a time, and you say out loud which one.
  3. When finished, all forces are removed, and you check that the warning LED has gone out.
Safety does not depend on the standard programA force can bypass the PLC logic, but it must not be able to bypass a well-designed safety function. An emergency stop or an interlocked door cuts the energy through its own safety circuit. If on your machine a forced output can move something with the door open, the problem is in the design.

Motor direction of rotation

The first start of each motor is a short bump, if possible with the motor uncoupled from the mechanics. On a three-phase motor connected directly to the mains, if it turns the wrong way you swap any two phases, always with the power off.

L1 L2 L3 L1 L2 L3 M 3~ M 3~ L1 to U, L2 to V, L3 to W: turns one way L1 and L2 swapped: turns the other way
Swapping any two phases reverses the rotating field and, with it, the motor’s direction of rotation.

If the motor runs on a variable frequency drive, the order of the input phases does not affect the rotation: the drive generates its own output. The direction is changed with a drive parameter or by swapping two phases between the drive and the motor.

Valves and analog signals

5. Validate the safety functions before moving the machine

Before running real cycles, each safety function is tested, one by one, and the result is recorded:

Typical mistakeBridging a safety device “to be able to get on” and forgetting to remove the bridge. It is one of the classic causes of accidents during commissioning. A safety device that gets in the way is fixed, not defeated.

6 and 7. Functional tests

  1. Manual: each movement on its own, at slow speed, checking limit switches and end stops.
  2. Automatic dry run: the full cycle with no product.
  3. With product: slowly at first, then at the real rate.
  4. Induced faults: cover a sensor, cut the air, open a door mid-cycle. The machine must stop safely and show a message people can understand.

Working with the programmer on the phone

Many commissionings are done with the programmer connected remotely or on the phone. Communication is half the job:

What is saidWhy
“I’m going to press the stop on desk 2, it should be I0.0”Both know what to expect before acting
“Confirmed: I0.0 goes to 0”Repeating what you see avoids misunderstandings
“Can I force Q2.0, cylinder down?” “Area clear, go ahead”No movement without permission from whoever is in the field
“I’ve moved the wire from terminal X2:14 to X2:15”Every change in the field is announced and marked on the schematic

Remote access to the PLC must also be secure: only when needed, with the customer’s permission, over a protected connection, and disconnected afterwards. A machine with permanent, uncontrolled remote access is an open door to anyone.

8. Handover: the machine comes with paperwork

Typical mistakes

Summary

Test what you have learned