Panel components and sensors

Level: Basic 8 min read 44 questions

Opening a control panel and knowing what each device is, what it is for and how it fails is the foundation of any technician. A good PLC programmer needs it too: you cannot program a machine well without understanding what the contactor behind each output does or why a sensor does not see a part. This topic covers the components you will find in almost every panel and machine: protection, switching, sensors and pneumatics. It follows IEC practice, with notes where North American practice differs.

Protection: the miniature circuit breaker

The miniature circuit breaker (MCB) protects the cables of the installation against two different problems:

Its main ratings are the rated current (for example 10 A or 16 A), the breaking capacity (the highest short-circuit current it can safely interrupt, for example 6 kA or 10 kA) and the curve, which says at how many times the rated current the magnetic part trips.

Curve B Curve C Curve D 3 to 5 × In 5 to 10 × In 10 to 20 × In 0 5 10 15 20 × In
Magnetic trip zone of each curve, in multiples of the rated current (In). The higher the curve, the more starting current it tolerates.
Common mistakeFitting a bigger breaker «because it keeps tripping». If the cable is the same, you have left the cable unprotected. If it trips, find out why: a real overload, a short circuit or a curve unsuited to the load's inrush.

The residual current device

The residual current device (RCD, also RCCB, or GFCI in North America) compares the current going out with the current coming back. If some is missing, it is leaking to earth, and it trips. It protects people (30 mA in IEC installations; 5 mA GFCIs in North America) and against fires caused by leakage (less sensitive ones, such as 300 mA). It does not protect against overload or short circuit: that is the breaker's job.

There are several types depending on the leakage currents they detect. Type AC only detects sinusoidal AC leakage; type A also detects pulsating DC; type B also detects smooth DC, such as a three-phase variable frequency drive can produce. That is why drive manufacturers state which type to use.

The test button (T) should be pressed periodically: it checks that the mechanism trips.

The motor protection circuit breaker

A motor protection circuit breaker (MPCB, or manual motor starter) combines magnetic short-circuit protection and adjustable thermal overload protection in one device designed for motors. It is set to the rated current on the motor nameplate. Many have auxiliary contacts so the PLC knows if it has tripped.

The contactor

A contactor is an electrically operated switch: when its coil is energised, it closes its contacts. It lets a small PLC output (24 V, a few milliamps) switch a motor drawing many amps.

1 3 5 13 21 A1 2 4 6 14 22 A2 power auxiliary coil
Contactor terminals: power contacts 1-2, 3-4 and 5-6; normally open auxiliary 13-14; normally closed auxiliary 21-22; coil A1-A2.

The numbering follows a logic that applies to many devices:

Contactors are chosen by utilization category: AC-3 is for squirrel-cage motors started and stopped in normal running. A 9 A AC-3 contactor can switch a motor of about 4 kW at 400 V.

You can watch a contactor working in its two most common circuits, start-stop with seal-in and forward-reverse with interlocks, in the motor control circuit simulator.

Interface relays

They separate the PLC output from the load: the PLC output only feeds the relay coil, and the relay contact feeds the load. They protect the output card and let you switch other voltages.

Surge suppressionSwitching off a coil produces a voltage spike that can damage the output that drove it and cause interference. DC coils get a diode in reverse across them (flyback or freewheeling diode); AC coils get an RC snubber or a varistor. Many relays and contactors include one or offer it as an accessory.

Sensors

SensorDetectsDetails
Inductive proximityMetal onlyShort ranges, a few millimetres. Very robust.
Capacitive proximityAlmost any materialUseful for liquid or granule levels, even through a plastic tank.
Through-beam photoelectricObjects breaking the beamSeparate emitter and receiver. The longest range.
Retro-reflective photoelectricObjects breaking the beamEmitter and receiver in one body, with a reflector opposite.
Diffuse photoelectricObjects reflecting lightNo reflector: it detects the light the object itself sends back.
Cylinder magnetic (reed)The piston magnetMounted on the cylinder barrel to detect its position.
Limit switchMechanical contactA lever or plunger operates a contact.

Besides the type, the output matters: PNP (sourcing, gives +24 V when it detects) or NPN (sinking, connects to 0 V when it detects), and normally open or closed. Three-wire sensors are powered separately (brown +24 V, blue 0 V, black output); two-wire sensors are in series with the load and let a small leakage current through even when not detecting, which is sometimes enough to turn on a sensitive input.

You can wire a PNP or NPN sensor to a PLC input, wire by wire, and see where the current flows in the PNP and NPN sensor simulator.

Pneumatics

Compressed air moves cylinders and grippers. It reaches the machine, usually at about 6 bar (90 psi), through an air preparation unit (FRL): filter (removes water and particles), pressure regulator (sets the working pressure and holds it) and, sometimes, lubricator.

Solenoid valves and their names

Valves are named with two numbers: ports / positions.

By how they return to position:

Speed and pressure

Pilot lights and push buttons

Pilot light colours have a standard meaning on machines (IEC 60204-1): red, emergency or danger; yellow, abnormal condition; green, normal condition; blue, mandatory action; white, neutral information. The emergency stop is red on a yellow background.

How components fail

Summary