Electrical safety and lockout/tagout

Level: Basic 7 min read 43 questions

A control panel holds more than enough energy to kill a person, and most accidents are caused not by a lack of knowledge but by haste: «it will only take a minute», «I have already switched it off», «it surely is not live». The five safety rules (often called the five golden rules) and lockout/tagout exist so that working dead does not depend on memory or luck. They are few, they are learned in a day and they protect a whole working life.

What current does to the body

What causes harm is not the voltage itself but the current flowing through the body and how long it lasts. At supply frequency, roughly:

Approximate currentEffect
Around 0.5 mAA tingle starts to be felt.
Around 10 mAMuscle contraction: you may be unable to let go of what you are holding.
Tens of mA for long enoughDifficulty breathing and risk of ventricular fibrillation, which can be fatal.

Besides current through the body there is the arc flash: an accidental short circuit, for example with a tool, can produce an explosion of heat and light that causes severe burns without anyone touching a conductor. That is why a short circuit in a power panel is as dangerous as direct contact.

The 30 mA RCDHigh-sensitivity residual current devices (30 mA, or 5 mA GFCIs in North America) trip when they detect leakage to earth of that order, and greatly reduce the risk from touching a part that has become live through a fault. They are a vital protection, but not an excuse: an RCD does not protect you if the current flows from one phase to another through your body without leaking to earth.

The rules behind it

Every country has its own law, but the ideas are the same everywhere. In Europe, the standard EN 50110-1 on the operation of electrical installations sets out the five safety rules, and each country's regulations build on it. In the United States, OSHA requires the control of hazardous energy (lockout/tagout, 29 CFR 1910.147) and safe electrical work practices, and NFPA 70E details how to apply them. The common principles:

The five safety rules

1 Disconnect every source 2 Lock out padlock and tag 3 Verify absence of voltage 4 Earth and short- circuit 5 Protect nearby live parts
The five rules, always in this order. The third, verify, is the one that saves the most lives.

1. Disconnect

Open every device that can feed the part you will work on, with an effective break: an isolator (disconnect switch), a switch with a reliable position indicator, or fuses removed. Every source: besides the main supply there may be a UPS, a second incomer, a generator, a control supply coming from another panel, or capacitors still charged.

Common mistakeSwitching off the circuit breaker and forgetting that the contactor's control supply comes from another panel, or that the drive has charged capacitors. After switching off a drive, wait for the time the manufacturer states, usually several minutes, and measure before touching.

2. Secure against reconnection: lock out and tag out

Make sure nobody can switch back on while you work. The method is lockout/tagout: a personal padlock on the isolator or on a lockout device, and a tag with your name, the date and the reason.

Isolator open (0) 1 2 3 Each person fits their lock. Only they remove it. One lock on: no switching on.
With a lockout hasp, several people can lock out the same isolator. While one lock remains, nobody can switch on.

Lockout rules that are not negotiable:

Not just electricityA machine holds other hazardous energies: compressed air, oil under pressure, parts that can fall under their own weight, loaded springs. Before putting your hands in, bleed the air, release the pressure and block any load that can move under gravity.

3. Verify the absence of voltage

Never assume there is no voltage because «it has been switched off». Test at the point of work, on every live conductor and also between them and earth, with suitable equipment: a voltage tester or a multimeter of the right measurement category.

And the procedure is always the same: test the tester on a known live source, test the point of work, then test the tester again (live-dead-live). If the tester failed along the way, a «0 V» reading means nothing.

4. Earth and short-circuit

The conductors at the point of work are connected together and to earth with equipment designed for it. That way, if someone switched on by mistake or voltage appeared by induction, the current would take that path and trip the protection instead of passing through the person. It is always required at high voltage; at low voltage, when the installation could become live accidentally, for example through induction or backfeed.

5. Protect against adjacent live parts and mark the area

If live parts remain near the point of work, cover them with insulating screens or shrouds, and mark out and sign the work area. Standards set approach distances that depend on the voltage (NFPA 70E calls them limited and restricted approach boundaries, and adds an arc flash boundary); follow the ones that apply where you work.

Re-energising

Restoring power is done in reverse order and with the same care: finish the work, warn everyone and check nobody is left in the area; remove the tools and the earthing equipment; each person removes their own padlock; and only then switch on.

Equipment and tools

24 V deserves respect too

24 V control circuits are not usually dangerous to touch, but the same panel has 230 V and 400 V (or 120 V and 480 V) a few centimetres away. Working «on the control side» with the panel live is working near live parts. And a short circuit on a powerful 24 V supply can melt cables and cause burns.

Common mistakes

Summary