Practical electrical theory

Level: Basic 5 min read 35 questions

The electrical theory used every day in a control panel fits in a few formulas: Ohm's law, power, the difference between phase and line voltage, and power factor. Using them fluently lets you check whether a measurement makes sense, choose a protective device or explain to a customer how much it costs to keep a motor running. This topic goes over them with workshop examples.

Basic quantities

QuantityUnitWhat it is
Voltage (U or V)volt (V)The «pressure» that pushes the current: the potential difference between two points.
Current (I)ampere (A)The amount of charge flowing.
Resistance (R)ohm (Ω)The opposition to the flow of current.
Power (P)watt (W)The energy per unit of time that a device uses or delivers.
Energy (E)kilowatt-hour (kWh)Power multiplied by time: what the utility bills you for.

Ohm's law and power

U = I × R  ·  P = U × I (in DC and with resistive loads)

Example: a 2 kW heating element on 230 V draws I = 2000 / 230 ≈ 8.7 A. A 24 V relay coil of 480 Ω draws 24 / 480 = 0.05 A. If you want to practise, the Ohm's law calculator solves any combination.

Resistors in series and in parallel

This explains a measurement that confuses many people: if you measure a resistor without disconnecting it and there is another one in parallel, the meter reads less than expected.

The heat of the current

A conductor of resistance R carrying a current I heats up with a power of I² × R (Joule heating). Note the square: if the current doubles, the heat is multiplied by four. That is why cables are sized for the current they will carry, why a loose terminal (more resistance) gets hot, and why protective devices interrupt overloads.

Alternating current

The supply completes 50 cycles per second (50 Hz in Europe and much of the world) or 60 (60 Hz in North America), and in each cycle the current reverses twice. When we say «230 V» we mean its RMS value, the one that produces the same heat as 230 V DC. The peak value is √2 times larger: about 325 V. Multimeters measure RMS (True RMS meters do it correctly even with non-sinusoidal waveforms).

Phase voltage and line voltage

In a three-phase supply, the voltage between two phases (line voltage) is √3 times the voltage between phase and neutral (phase voltage): 400 V ≈ √3 × 230 V. In North America you find the same ratio in 208 V ≈ √3 × 120 V and 480 V ≈ √3 × 277 V. That is why in a European panel you measure about 400 V between phases and about 230 V between phase and neutral.

AC power and power factor

With motors, transformers and coils, the current is out of phase with the voltage, and three powers appear:

P active (W) Q reactive (var) S apparent (VA) φ cos φ = P / S
The power triangle: S² = P² + Q². The power factor, cos φ, tells you what share of the apparent power is useful.

The active power formulas:

Example: a three-phase motor on 400 V drawing 10 A with cos φ = 0.85 takes P = 1.732 × 400 × 10 × 0.85 ≈ 5.9 kW from the supply.

Why power factor mattersWith a low cos φ, more current flows for the same useful power: more heavily loaded cables, more losses and, on many industrial tariffs, a charge for reactive energy. It is corrected with capacitor banks, which supply the reactive power close to the loads.

Energy and cost

energy (kWh) = input power (kW) × hours

Example: a motor with 4 kW of output power and 88 % efficiency takes about 4.55 kW. Running 8 hours a day for 220 days a year it uses 4.55 × 8 × 220 ≈ 8,000 kWh. At 0.15 per kWh (in euros or dollars), that is about 1,200 a year. That is why a more efficient motor, or a drive on a pump that does not always need full speed, can pay for itself quickly.

Overload and short circuit

Common mistakes

Summary

Test what you have learned

35 practical questions with explained answers. Free, no sign-up.

Start the test