How to use a multimeter safely and correctly

Level: Basic 12 min read 38 questions

The multimeter is the tool you use most in a control panel, and also the one that causes the most accidents when it is used wrongly. Measuring well is not just reading a number: it means choosing the right function, putting the probes in the right place, understanding what the reading tells you and, above all, not turning the meter into a short circuit. A technician who measures with a method finds a fault in minutes; one who measures blindly can spend the afternoon replacing parts that were fine.

What a multimeter measures

FunctionUsual symbolWhat it is used for in a panel
AC voltageV~ or VACMains supply (230/400 V, 120/240 V, 480 V), transformer outputs
DC voltageV⎓ or VDC24 V control circuits, PLC inputs and outputs, 0–10 V signals
ResistanceΩCoils, temperature sensors, motor windings
ContinuitySpeaker symbolWires, fuses, push button and relay contacts
CurrentA or mASmall loads and 4–20 mA signals
DiodeDiode symbolDiodes and bridge rectifiers

Many multimeters are auto-ranging: you choose the quantity and the meter finds the range. If the display shows OL (overload), the value is out of range: on resistance or continuity it means "open circuit".

For large currents you use a clamp meter, which measures without opening the circuit. Many clamp meters also include the functions of a multimeter.

Before you measure: safety

A control panel has more than enough energy to do serious harm. A short circuit through the meter can create an arc flash with severe burns, even if nobody touches a wire. So, first of all:

Typical mistakeMeasuring voltage with a lead left in the amps jack. That input has almost zero resistance: the meter becomes a short circuit between the two points. In the best case its fuse blows; in the worst, there is an arc flash in your hands. Always look at where the leads are before touching anything.

To work on a circuit, measuring is not enough: it must be isolated, locked out and tagged, proved dead with a suitable tester and, where needed, earthed. Our electrical safety topic explains the five safety rules step by step.

Measuring voltage: always in parallel

Voltage is a difference between two points, so the probes go in parallel with what you want to measure, without opening anything. The multimeter has a very high internal resistance (about 10 MΩ on digital meters), so the circuit hardly notices it.

Voltage: in parallel Current: in series 24 V 24 V load load V A nothing is opened the circuit is opened
Voltage is measured in parallel with what you are interested in. Current forces you to open the circuit and put the meter in series, unless you use a clamp meter.

Values you will find

When measuring DC, the red probe goes to the point you think is more positive and the black one to the reference (0 V). If you swap them, a digital meter shows the value with a minus sign: no harm done, but it is telling you the probes are the wrong way round.

Fault finding by measuring voltage step by step

Imagine a contactor will not pull in. Its coil gets 24 V through a chain of contacts in series: stop button, overload relay, limit switches… With the black probe fixed on 0 V, move the red one from the power supply towards the coil. Where the 24 V disappears, the open contact or the broken wire is between that point and the previous one.

The contact ruleMeasuring across the two terminals of the same contact, with the circuit powered: if the contact is closed, you read almost 0 V; if it is open, you read almost the whole supply voltage. It sounds backwards, but it makes sense: no voltage "drops" across a closed contact, and an open one takes the whole difference.

Ghost voltage

A wire disconnected at one end that runs in the same trunking as live wires can show tens of volts on the multimeter, sometimes more than 100 V AC. It is not a real voltage that can power anything: it is capacitive coupling with the neighbouring wires, which the meter picks up because its input resistance is so high.

To find out, some meters have a low impedance (LoZ) function: it places a low resistance between the probes that makes the ghost voltage disappear, while a real voltage stays. It is not used on sensitive electronic circuits, because that load can affect them.

True RMS and drives

With waveforms that are not sinusoidal, such as those produced by variable frequency drives, switch-mode power supplies or LED lighting, an ordinary multimeter can give wrong readings. True RMS meters measure those waveforms correctly. Even so, the output of a drive is hard to measure: some meters include a dedicated low-pass filter for it.

Measuring current: in series or with a clamp

To measure current with a multimeter you have to open the circuit and make all the current flow through the meter: the red lead moves to the A or mA jack. Those inputs are fuse-protected and have a limit, usually 10 A at most. That is why, in practice, the multimeter is used for small currents and 4–20 mA signals, and the clamp meter for everything else.

The clamp meter

A clamp meter measures the magnetic field created by the current flowing through a conductor. Advantages: you do not need to open the circuit or touch live parts. One condition: the clamp must go around a single conductor.

L L N One conductor Line and neutral together measures the load current reads almost 0 A out and return cancel out
Cross-section view: the clamp must go around a single conductor. With line and neutral inside, the currents flow in opposite directions and the result is almost zero.

If you clamp the whole cable of a motor or a single-phase appliance, the meter will read practically zero, because the current that goes out on one conductor comes back on another. That effect has a use: if you clamp all the live conductors and the reading is not zero, some current is escaping by another path, such as a leakage to earth. That is how electricians track down why an RCD or a GFCI keeps tripping, with leakage clamps that are much more sensitive.

On a balanced three-phase motor, the three phases should draw about the same. If one draws clearly more than the others, something is wrong: a damaged winding, a loose connection or a phase with low voltage.

The 4–20 mA signal

Many industrial sensors, such as pressure, level or temperature transmitters, send their reading as a current between 4 and 20 mA. 4 mA is 0 % of the range and 20 mA is 100 %. Current is used instead of voltage because it is not affected by the length of the cable or the resistance of the connections, and starting at 4 mA makes a broken wire detectable: 0 mA is not "zero", it is a fault.

To convert current into a value:

value = (I − 4) / 16 × range

Example: a 0 to 10 bar pressure transmitter sends 8 mA. (8 − 4) / 16 × 10 = 2.5 bar. And 12 mA, half of the current scale, is exactly 50 %: 5 bar. The 4–20 mA converter does this for any range.

There are three ways to measure it: open the loop and put the multimeter in series on the mA range, use a milliamp clamp or, if the PLC input has a known resistor, measure the voltage across it. With 250 Ω, for example, 4–20 mA becomes 1–5 V.

On siteThe programmer calls you to say the PLC reads 0 mA from a transmitter. Before replacing the transmitter, check that the loop has power and look for a loose terminal or a broken wire. A faulty transmitter is much less common than a bad connection.

Resistance and continuity: always with the power off

To measure resistance, the meter injects a small current and measures the voltage across the part. If the circuit is live, the reading is meaningless and the meter can be damaged. That is why these measurements are always made with the power off, and ideally with the component disconnected: if it is still wired in, other parallel paths can give a false reading.

To know what a resistor should read from its colour bands, use the resistor colour code calculator.

A multimeter does not test insulationA motor that shows no continuity to earth on the multimeter does not have proven good insulation. Insulation is tested with an insulation resistance tester (megger), which applies test voltages of hundreds of volts. A multimeter only finds dead shorts.

Three-wire PNP and NPN sensors

Three-wire inductive, capacitive and photoelectric sensors usually follow this colour code: brown to +24 V, blue to 0 V and black is the output. What changes is what the output does when it detects:

This splits the problem in two. If the sensor detects and there are 24 V on the black wire but the PLC does not see the input, check the terminal, the input card common and the configuration. If there are no 24 V, the problem is the sensor, its supply or its adjustment. And an obvious first check: the sensor must be the type the input card expects. An NPN sensor on a card wired for PNP will not work. The PNP and NPN sensor simulator lets you try both.

Typical mistakes

Practise without riskIn the multimeter simulator you can measure on a three-phase supply, a 24 V control circuit and a 4–20 mA loop, make the mistakes in this topic with no consequences and find faults by measuring point by point.

Summary